1/ Oh hai Clinical Excellence Commission @NSWCEC. Looks like you wrote an IPAC Manual for Quarantine Hotels recommending air pressure differential limits without considering the implications. Would you like some assistance with that? THREAD...
2/ Allow me to introduce you to Bernoulli's Equation as it pertains to flow through an orifice. In this case, under and around a door.
3/ Bernoulli's equation allows us to predict airflow from a pressure difference, and vice-versa. The Florida Energy Center tested various orifices for flow & pressure difference. ba-pirc.org/casestud/retur… Using these results I calculate a Cd of 0.71 for various slots.
4/ Not wanting to be wrong, I confirmed this at home. I measured the gap dimensions under a bedroom door, the air pressure difference, the flow entering the room, and the average velocity across the bottom of the door into the hallway with a mini vane anemometer traverse.
5/ For a 2.2 Pa positive pressure in the room relative to the hallway, the flow was 33.4 CFM (16 L/s) and average velocity 235 fpm (1.2 m/s) into the hall. I noticed at one edge the flow was reversed, entering the room. It was also much higher in the center.
6/ With the measured crack area and 2.2 Pa the calculated values are 16 L/s and 1.4 m/s, so the measurements match well with the model. The velocity measurement is difficult to make, especially with the reversed flow, so it makes sense it would be a bit lower.
7/ Turning to @NSWCEC's IPAC manual, it has a cutoff of up+5 Pa pressure difference (room higher than corridor), where "the room has very low risk of particles leaving the room when the door is opened".
Except there is always a crack, usually by design, and air flows freely.
8/ The crack under the door is there for typical corridor positive-pressure makeup air. If an exhaust fan is running, the makeup air has to come from somewhere. Positive pressure in the hallway keeps odours in the suites and supplies fresh air.
9/ It turns out that average velocity is independent of the area. In the limit the crack may become sharper, affecting the discharge coefficient, but otherwise this chart shows the average air velocity through a crack for a Cd of 0.71. Why allow up to 5 Pa?
10/ Shouldn't it be negative? A 3 Pa positive pressure still shoots air out into the hallway through a crack at 1.6 m/s. Why is that "low risk"? Here's an example from @drajm in a Perth hotel:
11/ I get it, this stems in part from the quarantine leak report which cited opening and closing of doors. Were differential pressures measured? Pressure is fundamental to airflow between zones.
12/ If the door is very tightly sealed with a gasket you can achieve very little air flow (volume) and the pressure difference will likely *increase*. But sealing gets only a very short mention once. How likely will this be done?
13/ Also, the door should only be completely sealed if it is compatible with the design of the building system. This is likely only for compartmentalization, where every suite has a dedicated supply and exhaust system and is air sealed from the rest of the building.
14/ Without compartmentalization the gap is needed for makeup air. With a gap, you need to ensure the suite is in negative pressure with continual exhaust.
15/ In typical hotels and apartments, opening windows messes with pressures and can cause all sorts of unpredictable airflow patterns.
16/ Here are recommended quarantine accommodation types, in order of preference, based on building science:
a) air-gapped
b) compartmentalized
c) negative pressure (with sealed windows).
17/ Looking at the contributors to this document I think we have an idea why this guidance is missing out on the fundamentals of fluid mechanics and building science that we've known for decades. Is @NSWCEC unintentionally practicing professional engineering here?
18/ There's many other problems with the NSW IPAC Manual for Quarantine Hotels that have been pointed out by others (cleaning is NOT an engineering control! gappy surgical masks instead of P2/N95 respirators for essential workers!) and I recommend heeding their advice.
19/ For further reading, I continue to add to a longer thread on the fundamentals of uncontrolled in air flow within buildings that can explain why there are outbreaks happening in apartment buildings as well as hotels, which have a similar design.
20/ @CathNoakes summarizes this thread well: "It’s the continuous flow under the doors that probably matters more than the brief flow when a door is opened."
21/ Overall the TooLongDidntRead summary is that because IPAC doesn't understand fluid dynamics they permit for airflow in the wrong direction that can lead to a repeat of transmission events within quarantine, which their guidance is trying to avoid in the first place.
22/ December update on this topic of pressure-driven under-door air flow from @CathNoakes
Vancouver Coastal Health has released an updated Ventilation and Indoor Air Quality resource for Schools and Childcare Facilities () but their CO2 page needs some edits. vch.ca/en/document-li…
Vancouver Coastal Health "CO2 concentrations do not indicate a risk of infectious disease transmission in a space". No.
ASHRAE's position document on indoor CO2 says "higher CO2 conc correspond to lower ventilation and potentially increased risk of airborne transmission"
Vancouver Coastal Health "Note that health effects from CO2 occur at levels above 5000 ppm". Did WorkSafeBC interfere? Because that's contradicted by your Health Canada reference in the sentence immediately before it.
This document has been a long time coming. As described by @jljcolorado, Lidia Morawska, co-chair of the group that published the new WHO airborne model, was previously cut off by John Conly when making the case that #COVIDisAirborne to WHO. /3
Air purifier manufacturers say HEPA should always be the filter of choice, and their product's proprietary filter delivers. Which HEPA? ISO 35H at 99.95% or ISO 40H at 99.99%? Why not ISO 50U? That's 10x better at 99.999%. Why stop there? Go for ISO 70U at 99.99999%! /1
The answer is, single-pass filtration efficiency DOESN'T MATTER except in specific cases like Powered Air Purifying Respirators (PAPR), clean rooms, operating theaters, or nuclear laboratory exhaust—HEPA's original purpose. /2
For portable/in-room air cleaners, all that matters is the Clean Air Delivery Rate (CADR) for a target particle size and type, within acceptable for sound power and frequency characteristics for the people in the room. /3
Four years into this and we can't keep duct-taping in-room filter solutions for clean air. It's just filter(s) and a fan. We need open-source, optimized design, certifiable product, efficient, repairable using commodity filters and commodity components. /1
We need air cleaners assembled and distributed by not-for-profit community-based social enterprise. No more lock-in to proprietary filters. Verified replacement commodity filtration performance for safety. /2
Low income with donated CR boxes will pay over time in electrical costs for the duct-taped solution for clean air.
Power utilization for Smoke CADR, same filters:
Conventional CR Box: 4 CADR/W. (77 W)
PC fan array air cleaner: 24 CADR/W. (8 W)
/3
1/ Levoit Core 400S versus Austin Air HM400 in a challenge to see which portable air cleaner removes submicron salt particle aerosols the fastest! Which do you think will win, and by how much? Poll in next tweet below...
2/ Which has a higher CADR (Clean Air Delivery Rate):
Levoit Core 400S, or Austin Air HM400?
See if you can find the manufacturer's claims for both, and then come back and vote:
[sarcasm] Not only is the Austin Air bigger and far heavier, it also draws way more power, is much louder, and more expensive. It couldn't possibly be *worse* than the Levoit, right? Right?