YAY for “tools to improve ventilation and air filtration” in WH plan

I often hear: too difficult, too $$$, wasn’t designed for it, everything’s fine.

As an engineer, I think it’s very doable. Doesn’t have to be $$$. Buildings are adaptable. We don’t know til we measure. 1/x
Where are ventilation and filtration now? What does improvement look like?

We wrote a paper on our 2020-now work:
From Guidance to Implementation: Applying ASHRAE Epidemic Task Force Building Readiness Strategies in 95 Commercial Office Buildings ashraem.confex.com/ashraem/w22/me…

2/x
We followed the ASHRAE Epidemic Task Force Guidance. There are 100s of pages of detailed guidance for engineers, facility operators, etc. High-level core recommendations here: ashrae.org/file%20library…
3/x
VENTILATION.

Goal: Provide and maintain *at least* the required minimum outdoor airflow rates.

What buildings should be doing, pandemic or not. We calculated required OA per ASHRAE 62.1-2019. Then measured OA, verified over time.

Re "minimums":
4/x
Result: Out of 95 buildings, about half (44%) already met current minimum ventilation rates.

About half were *under-ventilated*:
33% need minor adjustments to operations & maintenance (O&M) practices
23% need more significant work (retrofit, replacement)

5/x
Note that a new building didn't guarantee minimum ventilation rates were provided. Nor did an old bldg guarantee need for retrofits. Kind of even distribution of “in compliance” and “action needed: O&M” across years. More on the interesting pattern in 1980s buildings below.
6/x
33% need minor adjustments to O&M practices to meet or exceed min OA rate. Issues with actuators, sensors, control schemes, basic “stuff breaks”

Fix these, and we get to 77% of buildings that met minimum ventilation requirements at low effort / low cost! Such opportunity! 7/x
23% needed retrofits. Their original ventilation rates fall far short of current 62.1 rqmts. The 1980s were not great for IAQ standards! But HVAC equipment has ~25 yrs of expected service life so upgrades should be expected. These bldgs need investment - find them & plan now
8/x
For those already in compliance. Great!
What’s the plan to ensure it continues? Stuff breaks, weather changes.
For the hottest/coldest/smokiest day? People need (clean) OA at all times.
Opportunities to exceed the minimum ventilation rate?

9/x
That’s it for today. Filtration & conclusions for tomorrow.
For more technical deep dives in the HVAC trenches (on the rooftop?) @davidelfstrom and @joeyfox85 are putting out great twitter work. E.g.

10/x
Wow! So much enthusiasm for ventilation and filtration! The White House’s National COVID-19 Preparedness Plan (Mar 2022) has details on pages 81-83
whitehouse.gov/wp-content/upl…
11/x Give schools and businesses guidance, tests, and supplies to
Continued: Following ASHRAE ETF guidance (pic). Layered strategies for reduced exposure risk and better IAQ. Ventilation above.

FILTRATION.
Goal: Use filters & air cleaners to achieve MERV-13 (or better) performance on recirculated air.
“Typical” office bldg filter: MERV-8.
12/x Excerpt from ASHRAE Epidemic Task Force Core Recommendations
Result: In central systems, 90% upgraded to/already had MERV-13. 99% were technically capable of doing so.
Some “green” bldgs designed for MERV-13, didn’t have to scramble to upgrade.
1 bldg had no filter rack (!?) and will install a rack sized for MERV-13. MERV-8 for now.
14/x slide: Filtration: 90% of buildings upgraded to or already u
Some operators concerned about equipment limits
But can be calculated: filter rated pressure drop (PD) vs fan capacity. Get spec sheets, compare!
Higher MERV does not necessarily mean higher PD
Can find better filters w similar PD to existing filter

13/
What if your system can’t go to MERV-13?

Can it go to MERV-12, 11, 10…? Check the specs, do the math. No need to guess. ashrae.org/technical-reso…

Some bldgs. got MERV-11 as a compromise bc of lingering equip concerns. Still an upgrade.
15/x
What if your system can’t go to MERV-13 or you don’t control central HVAC?

In-room options: right-sized HEPA, engineered upper-room UVGI, and

*my favorite* option, the #Corsirosenthalbox!
engineering.ucdavis.edu/news/uc-davis-…
16/x
Sum:
Many buildings are under-ventilated, but many not too hard or $$ to fix now. Check HVAC often.
Find what needs upgrading (1980s?) & plan now
MERV-13 possible, do math now
Make #corsirosenthalbox

Many combos to better IAQ. We can figure out what’s possible / a priority
17/
Better vent & filt are doable, even with existing systems.

We know how. We need can-do attitudes! A la @CorsIAQ: Just do it!

Get worst-performers to min standards. Turn acceptable bldgs into healthy bldgs.

Design decisions last for generation+. What we do now matters.
18/end Conclusion slide: Risk mitigation and improved health outcom
@CorsIAQ BONUS, great papers on these issues in schools:
Vent. rates in CA classrooms: Why many recent HVAC retrofits are not delivering sufficient vent.
sciencedirect.com/science/articl…
Understanding teachers' experiences of vent. in CA K-12 classrooms and implication...
onlinelibrary.wiley.com/doi/epdf/10.11…

• • •

Missing some Tweet in this thread? You can try to force a refresh
 

Keep Current with Meghan McNulty

Meghan McNulty Profile picture

Stay in touch and get notified when new unrolls are available from this author!

Read all threads

This Thread may be Removed Anytime!

PDF

Twitter may remove this content at anytime! Save it as PDF for later use!

Try unrolling a thread yourself!

how to unroll video
  1. Follow @ThreadReaderApp to mention us!

  2. From a Twitter thread mention us with a keyword "unroll"
@threadreaderapp unroll

Practice here first or read more on our help page!

Did Thread Reader help you today?

Support us! We are indie developers!


This site is made by just two indie developers on a laptop doing marketing, support and development! Read more about the story.

Become a Premium Member ($3/month or $30/year) and get exclusive features!

Become Premium

Don't want to be a Premium member but still want to support us?

Make a small donation by buying us coffee ($5) or help with server cost ($10)

Donate via Paypal

Or Donate anonymously using crypto!

Ethereum

0xfe58350B80634f60Fa6Dc149a72b4DFbc17D341E copy

Bitcoin

3ATGMxNzCUFzxpMCHL5sWSt4DVtS8UqXpi copy

Thank you for your support!

Follow Us on Twitter!

:(