The three things you should do are: 1. Verify the building ventilation is working 2. Clean the air in your suite 3. Possibly block the airflow through the door (see below)
1/8
Verify the ventilation is working
The standard way ventilation systems work in hotels and apartment buildings is outdoor air is supplied to the hallway, flows under the door and is exhausted through the washroom. Here's how to check the ventilation:
2/8
1. Use a CO2 monitor. If it's high, you know something is wrong. 2. Go into the hallway and ensure air is being supplied. You can hold the CO2 monitor to the supply air and measure the CO2 being supplied. It should be around 420 ppm (100% outdoor air)
3/8
3. Hold a tissue to the exhaust grille in the washroom and ensure that air is being exhausted. 4. Check to make sure air is flowing under the door.
There might be units in the room for heating and cooling, but they only recirculate air. No ventilation.
4/8
If there are issues with any of this, notify the front desk.
Clean the air in the suite
Open windows and run a HEPA filter. It's best to place it near the door so you are filtering the air that is entering from the hallway.
5/8
Blocking the door
If the windows don't open and the system is working properly, it will be detrimental to block the door. Air is exhausted through the washroom and has to be replenished from somewhere.
6/8
If it doesn't come through the door, it could leak in through the walls of a different suite. So here's the rule:
- If the windows aren't open and the system is working (airflow through the door and up the exhaust) then do not block the door.
7/8
- If you have the windows open or the system isn't working (no air going through the exhaust), then block the door.
If you are blocking the airflow through the door, use painters tape around the door cracks to stop the airflow.
8/8
I was shipped this PC fan box and put it together. It looks really good. I think for many situations, this is the best option out there. Here are some thoughts about it.
1/11
I stated earlier on my blog: we need a PC fan air cleaner that is durable and looks good. While durability and looks are not the most important aspects of air cleaners, many companies want that. We now have it.
2/11
It took me about 1.5 hours to put together. It was a little more difficult than the @cleanairkits ones because Clean Air Kits uses plugs to snap the fans on instead of screws. This could be something adjusted in the future. 3/11
The blood libel is a deep scar from Jewish history. Jews were accused of slaughtering Christian children and baking their blood into the matzah we eat on Passover. It lead to pogroms against Jewish communities where many Jews were massacred.
We just witnessed a new blood libel created over the past day. Unverified claims by Hamas were promoted by MSF, the UN, politicians and many major media outlets.
We've seen the resurrection of all the classical antisemitism: pogroms, massacres, blood libels, death squads
This is a description of the Khmelnytsky massacres in Ukraine 1648–1649.
Since I first published this post, there have been multiple experiments showing ozone is a concern when using far-UV and needs to be taken into consideration.
In the post, I discuss how initially we didn't think it was a concern. I think ASHRAE needs to update their guidance on different UV wavelengths.
I have far-UV in my house. I think for personal residential use, it can be used in a limited way if you understand the risks with ozone and mitigate it with open windows when in use. That's how I use it.
Here are the equivalent clean airflow rates from the recent ASHRAE Standard 241 Control of Infectious Aerosols. I've calculated the equivalent air changes per hour and the equivalent CO2 (if all the clean air was outdoor air).
These rates are doubled when there is "vocalization above a conversational level" (e.g. singing)
I'll be hosting a space with the chair of the committee @WBahnfleth to discuss these rates and more. Please join and message for any questions you have. twitter.com/i/spaces/1gqGv…
To determine the ACH and CO2, I had to make assumptions about density and metabolic rate. I used values from ASHRAE standard 62.1 or found the closest approximation. If densities are different, the equivalent ACH would be different. It doesn't affect flow/person or CO2.
What should you ask about your indoor air quality?
There are things individuals can do to improve the IAQ in their own space, but it ultimately falls on the building owners and operators to provide clean air. Here are some things you should ask to know about the IAQ.
1/10
1. Outdoor Airflow (OA)
- Is the system constant volume or variable volume?
- If it is constant volume, what is the airflow to the room (in cubic feet per minute [CFM] or liters per second [lps])
- if it's variable volume, what is the max and min airflow?
2/10
- what is the minimum OA % supplied during occupied hours?
- what is the occupancy schedule?
- is the system always running during occupied hours/auto mode?
- how often is it checked and maintained?
"We need HEPA filtration, CO2 at 600 ppm and 100% outdoor air everywhere"
I see these types of comments non-stop. They are wrong and unhelpful. They show misguided ignorance about indoor air quality and what is actually required.
I'll start with filtration - you do not care about the filter efficiency. You care about the system effectiveness which is measured as a clean air delivery rate. MERV-13 with 300 cubic feet per minute (CFM) is identical to HEPA with 230 CFM. There's no reason to prefer HEPA.
Furthermore, air handling units can't handle HEPA filters. Demanding this is absurd when it will only increase cost and won't provide any benefit over MERV-13.
Having MERV-13 as the standard is sufficient for particulate matter issues.