Air purifier manufacturers say HEPA should always be the filter of choice, and their product's proprietary filter delivers. Which HEPA? ISO 35H at 99.95% or ISO 40H at 99.99%? Why not ISO 50U? That's 10x better at 99.999%. Why stop there? Go for ISO 70U at 99.99999%! /1
The answer is, single-pass filtration efficiency DOESN'T MATTER except in specific cases like Powered Air Purifying Respirators (PAPR), clean rooms, operating theaters, or nuclear laboratory exhaust—HEPA's original purpose. /2
For portable/in-room air cleaners, all that matters is the Clean Air Delivery Rate (CADR) for a target particle size and type, within acceptable for sound power and frequency characteristics for the people in the room. /3
HEPA-class filters aren't the optimal solution, unless that's all you are offering as a product. Instead, design for a system using a ISO 16890 or ASHRAE 52.2 rated filter, say ePM1 > 60% or MERV-13. These filters have far less restriction to airflow than HEPA filters. /4
A portable air cleaner designed to use a les expensive general ventilation filter can move substantially more air through it to achieve a greater CADR at low noise, and with lower electrical power consumption than a unit based on a HEPA filter. /5
And in case you are wondering, good quality general ventilation filters will remove health-damaging ultrafine submicron particles too, that optical particle counters can't even detect. /6
To recap, for in-room air cleaners, HEPA *IS NOT NEEDED*. What matters is the combination of filtration, fit, and airflow, to maximize the Clean Air Delivery Rate for a target particle type and size, verified by an independent laboratory test to an industry standard. /7
Addendum: This is why it doesn't matter if some brand of air purifiers aren't "HEPA" by a particular rating system, other than for faithful labeling & consumer trust (looking at you, Levoit). All that matters is the independent CADR test (looking at you, Austin Air). /8
FAQ: What about a vacuum cleaner? For that, you want high single pass filtration of a HEPA filter. That's one of the exceptions. A vacuum cleaner is horrible air cleaner (and can make the air worse with a weak filter), while an air cleaner is a horrible vacuum cleaner. /9
@joeyfox85 has written a post on this same topic. /10
@RolandSB13 If you crank up air speed to 52.2 levels, yes, you will see a much lower filtration level at the MPPS.
HEPA type filters are lab tested at a much lower velocity (~one fifth!). They would show lower filtration at MPPS if pushed to 52.2 speeds.
@daveberkeleyuk Hmmmm Dyson says the washable filter is HEPA. It's more likely a leak in the collection cylinder door, which is frequently opened and closed. Sometimes I'm not careful and it doesn't fully latch closed, then there's a REAL mess.
• • •
Missing some Tweet in this thread? You can try to
force a refresh
Vancouver Coastal Health has released an updated Ventilation and Indoor Air Quality resource for Schools and Childcare Facilities () but their CO2 page needs some edits. vch.ca/en/document-li…
Vancouver Coastal Health "CO2 concentrations do not indicate a risk of infectious disease transmission in a space". No.
ASHRAE's position document on indoor CO2 says "higher CO2 conc correspond to lower ventilation and potentially increased risk of airborne transmission"
Vancouver Coastal Health "Note that health effects from CO2 occur at levels above 5000 ppm". Did WorkSafeBC interfere? Because that's contradicted by your Health Canada reference in the sentence immediately before it.
This document has been a long time coming. As described by @jljcolorado, Lidia Morawska, co-chair of the group that published the new WHO airborne model, was previously cut off by John Conly when making the case that #COVIDisAirborne to WHO. /3
Four years into this and we can't keep duct-taping in-room filter solutions for clean air. It's just filter(s) and a fan. We need open-source, optimized design, certifiable product, efficient, repairable using commodity filters and commodity components. /1
We need air cleaners assembled and distributed by not-for-profit community-based social enterprise. No more lock-in to proprietary filters. Verified replacement commodity filtration performance for safety. /2
Low income with donated CR boxes will pay over time in electrical costs for the duct-taped solution for clean air.
Power utilization for Smoke CADR, same filters:
Conventional CR Box: 4 CADR/W. (77 W)
PC fan array air cleaner: 24 CADR/W. (8 W)
/3
1/ Levoit Core 400S versus Austin Air HM400 in a challenge to see which portable air cleaner removes submicron salt particle aerosols the fastest! Which do you think will win, and by how much? Poll in next tweet below...
2/ Which has a higher CADR (Clean Air Delivery Rate):
Levoit Core 400S, or Austin Air HM400?
See if you can find the manufacturer's claims for both, and then come back and vote:
[sarcasm] Not only is the Austin Air bigger and far heavier, it also draws way more power, is much louder, and more expensive. It couldn't possibly be *worse* than the Levoit, right? Right?
When an IAQ report for an elementary school states the acceptable industry CO2 guideline is 700 ppm above ambient, or 1200 ppm, ask why the professional is using Std 62.1-2016 Informative Appendix D that was DELETED in 2018 because of misuse and outdated 1950's data.
@O_S_P_E 's calculator will give a target steady state CO2 value based on Standard 62.1 minimum acceptable outdoor air ventilation rates. Hint: It's not 1200 ppm for an elementary classroom. Link: https://t.co/V1DwupuJ3xospe-calc.herokuapp.com
Key phrases identifying that the deleted Informative Appendix D was used:
-Target of 700 ppm CO2 above ambient
-ambient is 300-500 ppm
-majority of occupants be satisfied with respect to human bioeffluents
-uses 1.2 MET, 15 CFM (7.5 L/s), 0.31 L/min