@prlambert @energysmartwv @curious_founder One per room is way too many. They’re not small enough and the turndown isn’t low enough for that.
@prlambert @energysmartwv @curious_founder We usually do ducted #heatpumps for the whole house in our #HVAC design projects. When people come to us wanting all #ductless units, we try to talk them into ducted for the bedrooms.
@prlambert @energysmartwv @curious_founder Here's an example from a small high-performance house we did in Virginia.

Loads (in BTU/hr)

Bedroom 1
htg = 1,944
clg = 320

Bedroom 2
htg = 1,454
clg = 511

Study
htg = 1,665
clg = 1,063
@prlambert @energysmartwv @curious_founder The wall-mounted ductless unit we usually specify is the Mitsubishi MSZ-FS. The smallest one they make is a 6k unit.

Rated capacity (BTU/hr)
htg = 8,700 (at 47 °F)
clg = 6,000

Minimum capacity
htg = 1,600
clg = 1,700

See the problem?
@prlambert @energysmartwv @curious_founder One of those 6k ductless units in each of those 3 rooms will be running at the bottom of the range pretty much all the time.

The design heating lead is right around the minimum capacity, so you might get some benefit from the variable capacity on the really cold days.
@prlambert @energysmartwv @curious_founder The design cooling loads are way, way lower than the minimum capacity for the two bedrooms. That means they will never get any benefit from variable capacity.

The study has a cooling load closer to the min. capacity than the bedrooms, but it's still only 63%.
@prlambert @energysmartwv @curious_founder That analysis is for what happens at the design loads. 99% of the time, the house operates at part load conditions.

Finally, running at a capacity significantly higher than the load can lead to comfort problems.

• • •

Missing some Tweet in this thread? You can try to force a refresh
 

Keep Current with Energy Vanguard

Energy Vanguard Profile picture

Stay in touch and get notified when new unrolls are available from this author!

Read all threads

This Thread may be Removed Anytime!

PDF

Twitter may remove this content at anytime! Save it as PDF for later use!

Try unrolling a thread yourself!

how to unroll video
  1. Follow @ThreadReaderApp to mention us!

  2. From a Twitter thread mention us with a keyword "unroll"
@threadreaderapp unroll

Practice here first or read more on our help page!

More from @EnergyVanguard

Apr 16
Is humidity control just for warm-humid weather? Or can you grow mold in winter?

A little thread for the part of #energytwitter that hasn't seen the bigger picture of #buildingscience.

1/
First, if you think you're immune to moisture & mold problems because your climate is dry in summer, let me invite you to take a look inside your fridge. What's inside that container in the back that you've forgotten for a couple of months.

2/ Image
Extreme example: Family in Kansas had a poorly insulated building enclosure. They kept the inside relative humidity at 50% while outdoor temperature was -5 °F.

Yes, that's ice on the walls & ceiling inside the house. Here are the details:

3/

bit.ly/3vqD2GT Image
Read 11 tweets

Did Thread Reader help you today?

Support us! We are indie developers!


This site is made by just two indie developers on a laptop doing marketing, support and development! Read more about the story.

Become a Premium Member ($3/month or $30/year) and get exclusive features!

Become Premium

Don't want to be a Premium member but still want to support us?

Make a small donation by buying us coffee ($5) or help with server cost ($10)

Donate via Paypal

Or Donate anonymously using crypto!

Ethereum

0xfe58350B80634f60Fa6Dc149a72b4DFbc17D341E copy

Bitcoin

3ATGMxNzCUFzxpMCHL5sWSt4DVtS8UqXpi copy

Thank you for your support!

Follow Us on Twitter!

:(