@prlambert@energysmartwv@curious_founder One of those 6k ductless units in each of those 3 rooms will be running at the bottom of the range pretty much all the time.
The design heating lead is right around the minimum capacity, so you might get some benefit from the variable capacity on the really cold days.
@prlambert@energysmartwv@curious_founder The design cooling loads are way, way lower than the minimum capacity for the two bedrooms. That means they will never get any benefit from variable capacity.
The study has a cooling load closer to the min. capacity than the bedrooms, but it's still only 63%.
First, if you think you're immune to moisture & mold problems because your climate is dry in summer, let me invite you to take a look inside your fridge. What's inside that container in the back that you've forgotten for a couple of months.
2/
Extreme example: Family in Kansas had a poorly insulated building enclosure. They kept the inside relative humidity at 50% while outdoor temperature was -5 °F.
Yes, that's ice on the walls & ceiling inside the house. Here are the details: