1/ Clean Air Delivery Rate (CADR). The CADR of a portable filtration system is:

CADR = f x Q.

f is the fractional removal efficiency of particles that pass through a device (value = 0 to 1). Q is the volumetric flow rate of air through the device (e.g., m3/hr, ft3/min). ...
2/ A portable air cleaner may be highly efficient (high value of f) but also highly ineffective at removing particles from air if Q is very small. This is the case for a wide range of ion generators. Don't be fooled by claims of high efficiency. It's f x Q that matters.
3/ On the other hand, a portable filtration system might have a lower efficiency (say, 0.5) but a very high air flow rate that leads to significant reduction of particle concentrations in air. It is f x Q that matters.
4/ By its very name, CADR implies an equivalent amount of high quality (clean) outdoor air added to an indoor space (additional ventilation with clean air). Approximation of that ventilation equivalent is quite simple. Remember, it is f x Q that matters!
5/ The CADR for a device is usually given as a single number without units. In most cases the units should be scfm (standard cubic feet per minute). There are some companies that use cubic meters per hour, which is a bit deceiving as it makes the CADR look better than if in scfm.
6/ Make sure that when you see CADR = 300 or CADR = 500, etc., you know what units are being used. To convert from m3/hr to ft3/min simply multiply the former by 0.59. Or conversely, multiply ft3/min by 1.7 to get m3/hr.
7/ Here is an example conversion to a ventilation equivalent (EqACH) starting with CADR in ft3/min.

EqACH = CADR x 60 / (A x h)

Here, the "60" is to convert from minutes to hours. A is the floor area in ft2 and h is ceiling height in ft. EqACH has units of /hr, e.g., 3/hr.
8/ So, if a classroom has a floor area of 600 ft2 and ceiling height of 9 ft, a portable air cleaner with CADR = 300 ft3/min yields EqACH = 300 x 60 / (600 x 8) = 3.3/hr.
9/ If the actual ventilation rate of the classroom is 2/hr, this portable air cleaner leads to an effective ventilation rate (EVR) of 2/hr + 3.3/hr = 5.3/hr. That is a substantial increase and will help reduce virus-laden aerosol particles in classroom air.
10/ On the other hand, many ion generators have CADR closer to 50 ft3/min, leading to EqACH of 0.56/hr and EVR increase from 2 to 2.56/hr in the example above. Many ion generators also emit ozone that, in poorly ventilated classrooms, can be problematic (more in a future tweet).
11/ I used "approximate" above because not all classrooms approach well-mixed conditions and volume (A x h) is not really the empty volume. The volume of students, furniture, etc.., should be subtracted, but correction is small (< 10%). Approach FAR better than rule of thumb.
12/ It is important not to locate a portable filtration system near a wall or corner where air is recirculated from exhaust to inlet of the device. This can reduce effectiveness.
13/ Note that CADR is dependent on particle size, and that is why it is often given for smoke, pollen, and dust separately. For portable HEPA air cleaners the CADR values differ only slightly for these three types of particles (it is good across a spectrum of sizes).
14/ The Association of Home Appliance Manufacturers (AHAM) certifies CADR across the categories described above.
15/ For devices that use non-HEPA filters, make sure that you understand the filter rating. The difference in CADR for the particles listed above will vary to a much greater extent.
16/ The multi-sided MERV-12 or 13 DIY portable air cleaner with a box fan allows for high flows and can lead to high CADR across particle sizes of relevance to transmission of COVID-19. Follow @JimRosenthal4 for more information on these.
17/ Note that some portable air cleaners are being marketed to inactivate viruses in aerosol particles. The concepts described above are relevant for these devices as well. In these cases "f" is fractional inactivation and Q remains the air flow rate though the device.
18/ Before buying into these technologies, ask questions. What is "f"? What is Q for the device? What is their product? Does the device generate chemical by-products that may be irritating or worse for building occupants? Do these products persist in the indoor environment?
19/ Has the system been tested independently? Are the data from those tests available? This is not to say that these devices do not work well. But for now I am sticking with proven technologies and approaches. Much more to come ......

• • •

Missing some Tweet in this thread? You can try to force a refresh
 

Keep Current with Dr. Richard Corsi

Dr. Richard Corsi Profile picture

Stay in touch and get notified when new unrolls are available from this author!

Read all threads

This Thread may be Removed Anytime!

PDF

Twitter may remove this content at anytime! Save it as PDF for later use!

Try unrolling a thread yourself!

how to unroll video
  1. Follow @ThreadReaderApp to mention us!

  2. From a Twitter thread mention us with a keyword "unroll"
@threadreaderapp unroll

Practice here first or read more on our help page!

More from @CorsIAQ

5 Feb
B117 is spreading in US but we have not seen the explosion yet. Brace yourselves. These outcomes in Italy & Israel should give pause, a motivation for tripling down on reducing inhalation dose in all activities, and a quintupling down on layered dose reduction in schools. more..
Dose and risk reduction in schools must include re-opening plans based on extent of community spread, rapid exit plans, rapid testing if possible, rigorous and universal mask requirements, distancing and lower occupant density, pod groups, increased ventilation ....
supplemented with single zone filtration, e.g., portable HEPA air cleaner, to achieve at least 6 effective air changes per hour, as much outdoor activity (including teaching) as possible (I used to teach lectures on occasion outdoors in Texas - it can be done when elements allow)
Read 6 tweets
3 Feb
1/ SCHOOLS. A few days ago I watched the Director of the National Economic Council say we need children back in school so parents can get back to work. While that is one benefit, it should not be construed as the sole or even primary reason for wanting children back in school.
2/ The school environment is important for the mental, social, and in some cases physical growth of children. Remote learning has also led to an extraordinarily high virtual drop-out rate in many cities.
3/ But whether for schools that are already open or those that will be re-opened, we ought to invest in infrastructure that makes them substantially safer during this pandemic and healthier beyond the pandemic. It is not rocket science. Just do it!
Read 21 tweets
31 Jan
1/ It takes a lot to move higher education, but COVID-19 is doing it. Many in higher ed are looking at a much different future, certainly much more on-line education (that's been happening and will accelerate).
2/ Expect more in-person (face-to-face) lectures w/ simultaneous live-streaming and recording to provide students w/ options, less demand for on-campus housing and transportation services at many universities, universities providing greater IT support off campus, and more.
3/ There is potential for greater service to under-served communities and advancement in diversity, equity and inclusion with these changes. But there is also a risk of doing it wrong and a loss of sense of academic community and support.
Read 9 tweets
27 Jan
1/ I am seeing many interpreting this as "it's safe to send kids back to school." That's a misinterpretation. First, safe implies certainty, which is not true here. What can be said is that it is much safer to re-open schools if specific risk reduction measures are taken.
2/ Densely-populated, poorly-ventilated (the majority of schools I have studied in Texas) schools, especially during any periods when masks are not worn are a recipe for infection. Ask Israel.
3/ Proper layered risk reduction works, is not rocket science, and does not have to break the bank. More on LRRS in my webinar here:
Read 6 tweets
23 Jan
We are a couple of weeks away from the anniversary of the first known COVID-19 death in the US. In February 2020 the US had approximately 20 total deaths. As we move into February 2021 we will be pushing 500,000 deaths w/ a trajectory aimed much higher.
We failed a year ago. Infections got too far ahead of us. Our response should now be an all-out war to starve this virus & its new variants of hosts, to do what we should have done 10-11 mos ago. We can lower the future death total before vaccines get us to where we need to be.
The ABSOLUTE MINIMUM that must be done to reduce inhalation dose in both the near- and far-fields is (1) UNIVERSAL mask wearing in ALL indoor environments other than one's own home in the presence of immediate family, and (2) physical distancing of AT LEAST six feet.
Read 6 tweets
21 Jan
I agree w/ @linseymarr that lower than 800 ppm is often needed, but we also need recognition that what is a "safe" CO2 concentration in on environment may not be safe at all in another, and vice-versa.
The actual max acceptable value depends on # of people present, typical time spent in environment, mask requirements, respiratory minute volume, and effectiveness of controls.
For 25 people spending 2 hrs in the same indoor space, a rough estimate based on a quanta generation rate similar to that in Restaurant X is CO2 < 695 ppm for an infection probability of < 5% w/o masks or controls. Assuming worst (no masks or controls) provides a safety factor.
Read 7 tweets

Did Thread Reader help you today?

Support us! We are indie developers!


This site is made by just two indie developers on a laptop doing marketing, support and development! Read more about the story.

Become a Premium Member ($3/month or $30/year) and get exclusive features!

Become Premium

Too expensive? Make a small donation by buying us coffee ($5) or help with server cost ($10)

Donate via Paypal Become our Patreon

Thank you for your support!

Follow Us on Twitter!