This is a ~2000 sf 1950s Cape Cod in Cleveland Heights.
Full case study on the insulation and air sealing project we did here. It was about $20K and was focused in the attics of this house (it has 4, or was it 5?)
The house started off really leaky at 5800 cfm50 blower door. We got it down to 3100 cfm50. Still not great, but far better. And good enough it turned out.
The house fundamentally changed. The second floor wasn't 10 degrees warmer in summer anymore, it was within 2-3 degrees.
The house has a 2 stage 60kbtu furnace. Low stage is ~38kbtu output, close to a 3 ton heat pump.
Manual J was 57K. Reality at 5F is in the 27-30K range.
Here's the house in the 2/15 cold snap, the coldest February in Cleveland history iirc.
Here's the house that summer on two design days (88F). It has a 3 ton AC that is now WILDLY oversized.
A variable speed 2 ton would be appropriate, and could be set to sip energy at 25-40% capacity at peak times while keeping the house cool because the AC is still running.
This house is now a thermal battery.
It can get through a power outage without a lot of drama.
Would it be hard in a multiple day outage at 0-10F temps like Texas just saw? Yes. But post project this house would have a much lower chance of pipes freezing that pre project.
But there's a problem.
Few will see the value in spending $20K (or about $150/mo for 15 years) on a project like this, and looking back it should have been at least $5K more for good margins.
This client sold this house and got $0 extra.
His realtor said "oh honey, people don't care about that, they just care about how many bedrooms and bathrooms there are."
This is why we talk about resale value so much. This client pushed his retirement date back 1-3 years.
We're finding about 50% of houses can benefit from air sealing and insulation upgrades like this house got, but we just don't see a path to more than 3% actually upgrading.
There are 3 requirements to do these projects: 1) client must have problems worth spending $100-200/mo to fix 2) client must be able to get that money (without harming themselves financially!!!!) 3) client must plan to live in the house for long enough to enjoy benefits
~3%
Do you want to see more projects like this?
We need a contractor base for it. Which doesn't exist.
And a sales process. And sold projects.
Selling these projects is really f*cking hard. The path is crazy narrow. Executing well is hard too.
Only THEN does financing matter.
Only a few homes are going to do this. A lot of comfort issues can be solved with right sized variable speed HVAC, and we can always do hybrids (heat pump + furnace) for unimproved homes that aren't thermal batteries. Most will do that.
Hybrids reduce gas use 40-100% btw.
Here's the simplified HVAC 2.0 process. The project above went through the Comprehensive Planning Process and then a major upgrade. Note the % of each path, this is what we're seeing so far.
If we want resilient homes that are thermal batteries and can ride out crazy outages, we need to do upgrades like this.
But there aren't contractors to sell or do them. Then homeowners need to buy them.
And they have to be done pretty well or they don't work.
How do things get done well? Usually with competition - do a good job or look like an idiot.
That also leads to a race to the top on quality rather than a race to the bottom on price.
All of this is built into HVAC 2.0.
But the network is small still.
Want to help build it? Take the Electrify Everything Course to learn the details you need to know, thousands of hours of experience pared down into 4-5 hours of content, plus how to find a contractor.
Tight well insulated homes perform well, exhibit A:
This 5000 sf new home in Cleveland with an 80kbtu 98% furnace and 4 ton heat pump is only at 67% capacity at 8F. That’s about 53kbtu/18kw output.
A 4 ton heat pump would be appropriate here. For a huge house!
As we discuss resilience, air tightness is important. This house clocked a 1025 cfm50 blower door or about 1 ACH50.
Exhibit B: 2300 sf 1950 built ranch. 3 ton heat pump. 2000 cfm50. This heat pump shuts down automatically below 3 F. 5 kw/15,000 btus of backup heat is handling the house at this moment.
As painful as it is to watch what's going on in Texas, the residential solution basically looks like what we should be doing anyway:
-Tighter, more efficient homes
-Smaller, more efficient HVAC
-Batteries
-More local generation like community solar
Hard to sell tho!
The fact of the matter is we humans don't change until the pain of not changing is greater than the pain of changing.
In residential resiliency creating a comfortable, healthy, and efficient home is a great deal of work. Work that few contractors are good at selling or doing.
The situation in Texas brings up very valid concerns about electrification - how do we handle the really tough cold snaps?
The heat pump water heater price difference was outrageous!
$4600 is high for the midwest, but I can see it. $7000 is highway robbery. And I seldom give contractors a hard time for pricing.
That's what having fear priced in looks like, or not wanting the job.
Most of California can basically swap a furnace for a heat pump, although the experience with single stage equipment may be mediocre (loud and lots of blowing air.)
Cold climates need to swap very carefully or experiences will suck, which will act like an anchor on demand.
This is part of integrated project design - have a plan so you can hold everyone accountable. A duct design is not totally sacred, there will be challenges in the real world not reflected here, but it helps guide the project and deliver better results.
This isn't needed on every job, but it should always be available if needed.