More results involving Electronic Air Cleaners. This time using Hydrogen Peroxide in the air for air/surface disinfection (PCO + DHP).

I will focus on the air disinfection results.

Results are from a chamber test 👇.
Principle of work per manuf.: the device produces dry hydrogen peroxide with max concentration of 20 ppb that is able to last long enough to diffuse throughout the space (half life is 30 - 60 mins; for comparison: half life of ions is in the seconds).

trane.com/content/dam/Tr…
Result from the in-duct device (Name = Blade DHP) show that the device is not very effective to reduce airborne concentration (<10% effective).

Note: You will need to subtract natural decay curve.
Result from the in-room devices (Name = Sphere and Sentry) show that the devices are not very effective to reduce airborne concentration (<25% effective).

Note: You will need to subtract natural decay curve

• • •

Missing some Tweet in this thread? You can try to force a refresh
 

Keep Current with Marwa Zaatari

Marwa Zaatari Profile picture

Stay in touch and get notified when new unrolls are available from this author!

Read all threads

This Thread may be Removed Anytime!

PDF

Twitter may remove this content at anytime! Save it as PDF for later use!

Try unrolling a thread yourself!

how to unroll video
  1. Follow @ThreadReaderApp to mention us!

  2. From a Twitter thread mention us with a keyword "unroll"
@threadreaderapp unroll

Practice here first or read more on our help page!

More from @marwa_zaatari

17 Mar
I will show an equal love to another bi-polar ionization technology claiming the usual 99.99% and no by-products.

In this thread, I will discuss two studies one by FEMA/CDC and one by Bureau of Toxic Substance Assessment (BTSA) NY versus the manufacturer claims.
Manufacturer claims no (ZERO) ozone production. Published test on the website from an outside lab:
atmosair.com/wp-content/upl…

Test Date = 2005 Image
Independent testing by CDC/FEMA (1/2) - 2009:

After hurricanes Katrina and Rita, FEMA purchased provided temporary housing for families who were displaced by the storms and looked for air cleaners to reduce formaldehyde but decided first to test if they produce ozone.
Read 6 tweets
9 Mar
The defeat of ions.

Thread about Needle Point Bi-polar Ionization.

What the manufacturer claims versus what independent studies report.
@ShellyMBoulder @jljcolorado @JimRosenthal4
What the manufacturer claims?
I will focus on three claims: reduction of PM count by agglomeration, surface inactivation of COV-2, removal of VOCs + formaldehyde.
-GPS+MERV 8 reduced particle count concentration by 89.7%
-GPS report 99.8% SARS-COV-2 surface inactivation
What the independent studies by subject matter experts found (device tested is produced by GPS).

Claim of reduction of particulate matter concentration: False.

Source: sciencedirect.com/science/articl…
@stephensbrent @etgall
Read 8 tweets
15 Feb
1) About MERV 13 - upgrading filters to MERV13 is the cheapest and most consistent/ practical solution:
For a 10,000 ft2 school buildings or 15 classrooms, it only costs $546/YEAR. This simple upgrade will give you ~5 ACH.
2) About air purifiers, it costs equal or more than $250 to put 1 purifier in 1 classroom (500 ft2) to give ~5 ACH.

Here is a collection of air purifiers available on the market (fan + HEPA filter) compared by cost/ft2 and noise.
3) About ventilation (1/3): if the building open the outside air dampers as designed (per minimum code), you get an extra 4.23 ACH.

-> A lot of studies found that schools are under ventilated because the operators chose to save energy (closing the outside damper on purpose)
Read 5 tweets
10 Feb
If my school building was running the way it was supposed to be run (compliant to minimum codes), how would it rate per Harvard-CU Boulder Air Exchange Rate Target?

In other words, are we asking too much from school buildings? 🧵

@j_g_allen
Classroom
- 500 ft2, 12 kids
- served by a central AC system

To obtain the certificate of occupancy (to be allowed to occupy the classroom), this classroom need to have minimum outside air according to building codes. This is by design and should be kept in operation.
1) The minimum outside air equal to 2.7 ACH.
2) The AC system has a filter - mainly installed to protect the heating and cooling coil - of MERV 8 (pretty common in school buildings). The filter + airflow will get you 2.67 ACH.
Read 5 tweets
9 Feb
My school installed an electronic air cleaner system (EAC), what should I do?
1) Ask for the following (part 1):
-Make/model of the system
-What is the basis to choosing the number of units? How many units is needed for the airflow, number of people, ft2?
- How do we verify it is working after it is installed?
Ask for the following (part 2)
- Efficiency test data that correspond to the install (in-room versus duct?)
- By-products test (formaldehyde, ultrafine particles, ozone) test at the SAME conditions of the efficiency test.
Read 16 tweets
8 Feb
Here is a collection of cheating techniques of ionizers when reporting test results 🧵 @jljcolorado
1) Use a small chamber or position their equipment above a tiny surface (example Petri dish) when reporting efficiency to exaggerate the %.
For example, reported efficiency of an equipment positioned above a tiny surface is 93%. Applying to real conditions (duct, with appropriate surface area and contact time), this efficiency will be 0.0016%.
Read 7 tweets

Did Thread Reader help you today?

Support us! We are indie developers!


This site is made by just two indie developers on a laptop doing marketing, support and development! Read more about the story.

Become a Premium Member ($3/month or $30/year) and get exclusive features!

Become Premium

Too expensive? Make a small donation by buying us coffee ($5) or help with server cost ($10)

Donate via Paypal Become our Patreon

Thank you for your support!

Follow Us on Twitter!