🧵 about ventilation
- Mechanical versus Natural ventilation
- ASHRAE Standard 62.1 historical rates
- Why schools are under-ventilated?
- What is the cost of outside air?
- What we should do about it?
Note 1: According to ASHRAE Standard 62.1 (most prominent ventilation standard), ventilation is not only about outside air. Rather, it is the sum of outside air and return air that is cleaned.
In this thread, I will focus only on outside air.
Note 2: schools are either designed to have mechanical ventilation (intentional OA from HVAC unit) or natural ventilation (intentional OA through windows and doors).
Most schools in North America are mechanically ventilated (for many reasons mainly for comfort and safety).
Note 3: Ventilation rates from ASHRAE Standard 62.1 are minimum rates.
Every building need to comply with these rates at a minimum in order to be occupied. Buildings can not obtain certificate of occupancy without complying.
Mechanical Ventilat. case:
HVAC system lasts < 25 years, meaning that for old buildings HVAC was replaced > 1996.
To replace HVAC, you need a permit that shows that the new design complies with min OA rate 👇.
This means that schools have min OA (design) same or > 2019 rate.
Natural ventilation case - 1: some schools uses natural ventilation. But this is not a slam dunk... It carefully requires designing windows, opening sizes, airflow/studying outside air conditions (three pages requirement in the standard).
Natural vent -2: It will NOT work all the time. Ventilation experts warn that “simply opening windows and doors without the use of exhaust fan, does not ensure adequate filtration – dependent on natural driving forces caused by the difference in temp wind speed."
Natural vent -3: this is why Standard 62.1 requires every natural ventilation design to have a backup mechanical ventilation design.
If the building is NOT designed for natural ventilation, opening windows will not work all the time.
We know that schools are under-ventilated:
Lit. review By Dr. Fisk (2017) of studies with large # of classrooms: CO2 concentrations often far exceed 1000 ppm👇
OA rate was ~50% rate of Standard with some studies showing only 2 cfm/person.
Dr. @CorsIAQ reported similar results from a 4-yr study involving 7 high schools of different ages & construction, & 46 classrooms"
Why are schools are under-ventilated?
I wrote about this in 2018. Below are the dirty half dozens reasons to why buildings operate without ventilation and what should we do about it.
The problem applies to all buildings including schools.
@CorsIAQ reported that each schools they tested had mechanical ventilation with capability to increase OA.
The reason why schools were under-ventilated was to save energy (energy required to condition the outside air)
How much energy does outside air cost?
According to Fisk (2017), annual costs range from few dollars to max of $10 per person PER YEAR --> "small price to pay given evidence of benefits"
Minimum ventilation is key to decrease risk of transmission during COVID. Beyond COVID, there is a compelling evidence of association of increased student performance by few % to as much as 15%, reduced absence (and diseases) with ventilation (i.e., lowering indoor pollutants).
All of this to say is that schools should prioritize looking into their ventilation systems especially with the available relief money: 1) check what type of OA system (mech versus natural), 2) perform a test and balance, 3) determine maximum OA capability at worst conditions
There is NO excuse!!
We have a moral obligation to protect our children.
Money is available to be used for basic and proven strategies: outside air, mech. filtration, UV.
and should NOT be spent on adding chemicals to the air (No To Ionizers, UV-PCO, O3, DHP, etc.)
• • •
Missing some Tweet in this thread? You can try to
force a refresh
-How to achieve 10 L/s/Person (22 CFM/person) of outside air
-What does it mean in terms of 3’ to 6’ social distance.
-How to achieve >4 ACH
-Myths regarding air cleaning
Classroom: 960 ft2
Specific dimension: 30' x 32'
Number of occupants: 30 (this is the design number, taking into account average classroom density - pre COVID)
1) Ventilation
By code, this classroom would have 415 CFM of airflow of outside air. This airflow is being forced through the HVAC system (unit in classroom or mechanical room).
By code, when designed, every classroom in United States need to comply with this requirement.
Manufacturer claims no (ZERO) ozone production. Published test on the website from an outside lab: atmosair.com/wp-content/upl…
Test Date = 2005
Independent testing by CDC/FEMA (1/2) - 2009:
After hurricanes Katrina and Rita, FEMA purchased provided temporary housing for families who were displaced by the storms and looked for air cleaners to reduce formaldehyde but decided first to test if they produce ozone.
More results involving Electronic Air Cleaners. This time using Hydrogen Peroxide in the air for air/surface disinfection (PCO + DHP).
I will focus on the air disinfection results.
Results are from a chamber test 👇.
Principle of work per manuf.: the device produces dry hydrogen peroxide with max concentration of 20 ppb that is able to last long enough to diffuse throughout the space (half life is 30 - 60 mins; for comparison: half life of ions is in the seconds).
What the manufacturer claims?
I will focus on three claims: reduction of PM count by agglomeration, surface inactivation of COV-2, removal of VOCs + formaldehyde.
-GPS+MERV 8 reduced particle count concentration by 89.7%
-GPS report 99.8% SARS-COV-2 surface inactivation
What the independent studies by subject matter experts found (device tested is produced by GPS).
Claim of reduction of particulate matter concentration: False.
1) About MERV 13 - upgrading filters to MERV13 is the cheapest and most consistent/ practical solution:
For a 10,000 ft2 school buildings or 15 classrooms, it only costs $546/YEAR. This simple upgrade will give you ~5 ACH.