IMPORTANT NOTE for journalists and others reporting on this ERCOT generator outage data & #TexasBlackout #TexasFreeze:

ERCOT's reporting method for wind capacity outages overstates the impact of wind outages on reliability by about 4x.

Here's why...
The outages reported for wind in this report are based on reductions from the "Seasonal Max MW," which is the maxim rated capacity of the wind farm in the winter. But ERCOT wisely does NOT count on wind farms to produce 100% of their output (the wind is inconstant. Duh).
As the Winter "Seasonal Assessment of Resource Adequacy for the ERCOT Region" report details, ERCOT 'de-rates' wind during winter peak load events to account for its variability. The derate differs for wind in different regions, but the average derate is ~25% of the max capacity.
Here is the full SARA report ercot.com/content/wcm/li…

ERCOT also considers extreme low wind periods in their planning, and the system should be resilient to such events. That counts on as little as 1,791 MW of wind output.
In sum: ERCOT is never planning on 100% of wind farm output to help meet winter peak demands. They count on about 1/4 of the wind capacity on average, and should be reslient to as little as about 6% in extreme cases. So the outage report overstates impact of losing wind by >4x.

• • •

Missing some Tweet in this thread? You can try to force a refresh
 

Keep Current with JesseJenkins

JesseJenkins Profile picture

Stay in touch and get notified when new unrolls are available from this author!

Read all threads

This Thread may be Removed Anytime!

PDF

Twitter may remove this content at anytime! Save it as PDF for later use!

Try unrolling a thread yourself!

how to unroll video
  1. Follow @ThreadReaderApp to mention us!

  2. From a Twitter thread mention us with a keyword "unroll"
@threadreaderapp unroll

Practice here first or read more on our help page!

More from @JesseJenkins

6 Mar
Since rebound effects came up in my Voltscast chat w/ @drvolts' intro, a new paper by @steve_r_sorrell is timely! carbonbrief.org/guest-post-why…
"economy-wide impact of these effects and find they may erode more than half of the potential energy savings from improved energy efficiency."
Here's the lit review on rebound effects I wrote @TheBTI in 2011, which @drvolts mentions in the podcast. I inspired by the earlier work of @steve_r_sorrell at UKERC as well as @hsaunders6 thebreakthrough.org/articles/new-r…
Rebound effects describes phenomena where energy efficiency makes energy services (lighting, heating, industrial process) cheaper, inducing greater demand for those services (direct rebound), spending of savings on other energy using activities (indirect) + macroeconomic effects
Read 12 tweets
5 Mar
Ok time for a #EnergyTwitter crowdsource investigation: @ERCOT_ISO just released plant-level generator outage data from the #TexasBlackout. Here's a PDF ercot.com/content/wcm/li…

An Excel file is also out: dropbox.com/s/xz91kfbk0vvx…

Holler if you see anything notable! Ill do same.
No cause of outage information included though, so still requires some real guess-work as to what went wrong.

Focus on ~12:00am-2:00am February 15th period. That's when mass generator outages sent the Texas grid dangerously close to full system blackout. ercot.com/content/wcm/ke…
Like, what the heck was going on here with all of these natural gas plants failing over the course of two hours? Many correlated failures at multiple plants at about the same times (12:23-12:27am; 1:00am; 1:23-1:35am).
Read 8 tweets
25 Feb
Wow, this graphic from a new @ERCOT_ISO report on the #TexasBlackouts shows how close the ERCOT grid was to a cascading failure that could have easily blacked out the whole system. ercot.com/content/wcm/ke… 1/
Going into the night of Valentine's Day, February 14th, a new winter peak demand of 69,222 MW was set at 7:06pm. By 1:23am in the middle of the night on February 15th, frigid temps had left more than 35,000 MW of generating capacity offline. 2/
Faced with greater demand & diminished generation capacity, ERCOT, the grid operator, ordered transmission utilities to start disconnecting millions of customers. The initial order was to shed 10,500 MW of demand. This grew to a height of 20,000 MW by the end of Feb 15th. 3/
Read 11 tweets
24 Feb
A good look at the variability of wind and solar resources in Texas, from @VibrantCE. They show that wind power can exhibit significant inter-annual variability, and some extreme years exhibit winter months with near-zero output from wind. This is rare, but happens.
Solar exhibits less interannual & monthly/weekly variation than wind, but there is, of course, this thing called night. That said, batteries + solar can mitigate diurnal cycles well. So solar+storage can be counted on a bit more than wind it seems, with higher capacity value.
This variability needs to be accounted for in resource adequacy planning, including the potential for correlated extreme low wind events during periods of system stress.
Read 5 tweets
20 Feb
The Lessons of the Texas Power Disaster nyti.ms/2NfdrPv

Today's @nytimes editorial cites and echoes my recent op ed on what went wrong in Texas and what it means for building a cleaner & more resilient energy system.
For more on what went wrong in Texas, see my op ed in the @nytimes here
For a forward looking view on how to ensure adequate firm resources in a clean electricity system, my seminar on The Critical Role of Clean Firm Resources here:
Finally, check out this week's issue of @TheEconomist, which has a cover story building on the @Princeton Net-Zero America study about how the United States can regain it's leadership on #ClimateAction and build a clean energy economy
Read 4 tweets
19 Feb
It takes a lot of gall -- or deliberate ignorance -- to see widespread failures of gas wells, pipelines, & power plants resulting in days-long loss of ~28,000 MW of thermal power plants, mostly gas, and say, "this proves we need more gas and coal plants!"
Some facts on the #TexasBlackouts for @KimStrassel and others peddling false narratives that do nothing but mislead and distract from the key steps Texans need to take.

1. ERCOT news release confirms 28,000 MW of thermal plant outages (mostly gas) ercot.com/news/releases/…
2. "nearly half of the state’s natural gas production has screeched to a halt due to the extremely low temperatures, while freezing components at natural gas-fired power plants have forced some operators to shut down."

texastribune.org/2021/02/16/nat…

#TexasFreeze #TexasBlackout
Read 7 tweets

Did Thread Reader help you today?

Support us! We are indie developers!


This site is made by just two indie developers on a laptop doing marketing, support and development! Read more about the story.

Become a Premium Member ($3/month or $30/year) and get exclusive features!

Become Premium

Too expensive? Make a small donation by buying us coffee ($5) or help with server cost ($10)

Donate via Paypal Become our Patreon

Thank you for your support!

Follow Us on Twitter!