1/ #ONTed, Memo B14 says for non-mechanically ventilated classrooms, must size portable HEPA units & consider noise.

For equity with their mechanically ventilated counterparts, typical elementary classroom during instruction should add 400 CFM CADR & under 50 dB(A) total. Text as image for Ontario Ministry of Education memo B14 Aug
2/ A new portable classroom or newer school (~20-25 years) will have *more* than this minimum ventilation capability, AND lower noise, AND *additional* built-in filtration (like MERV-13 filters) So, this is an entirely realistic goal, that still doesn't fully achieve equity. Photo of an elementary school with multiple (unequal) types
3/ The Ministry recognizes the higher risk in unmasked (kindergarten) situations. To address elementary unmasked time (lunch!) in non-mechanically ventilated classrooms, capability should be double, so up to 800 CFM CADR, with *total* room noise under occupational safety limit. Text as image from ETFO Noise in Classrooms publication
4/ These recommendations come from ASHRAE Std 62.1 standard for ventilation, and various standards for acoustics as outlined by @ETFOeducators document Noise in Classrooms. etfohealthandsafety.ca/site/noise/
5/ Where does that put us with one of the most common air cleaners on the market?

Austin Air HM400 is nominal 400 CFM *without the filter*, and with the filter provides:
High 250 CFM & 65 dB(A)
Med 125 CFM & 55 dB(A)
Low 40 CFM & under 40 dB(A)
6/ The Austin Air units are good for other contaminants because of the large carbon filter component, as this detailed independent video review covers:
7/ For student equity with their peers blessed with the advantage of a mechanically ventilated classroom WITH additional high-MERV filtration AND extra outdoor air provision, one typical HEPA unit isn't going to cover it for a non-mechanically ventilated classroom.
8/ I'm sure my friend @joshpascoe would be eager to sell more units in Ontario to meet the requirements - run multiple units on lower speed for the noise component, with total capacity for more cleaning power during unmasked activities.
9/ Another example: Dufferin-Peel Catholic District School Board issued a tender (T2020-102) for industrial air scrubbers with noise on maximum speed of 79 dBA.
10/ So be aware, if sized for absolute minimum equivalency for mechanical ventilation without regard to noise, the total classroom noise may exceed occupational limits.
11/ As the Ministry of Education advises, work with qualified professionals, like Professional Engineers @O_S_P_E and Industrial/Occupational Hygienists who can do the necessary calculations and measurements.

If not, are board staff practicing engineering without a license?
12/ Finally, demand that @fordnation fund proper long-term capital improvements outlasting an election cycle to properly @Fix_Our_Schools!!
13/ See?? No professional oversight, result: THIS

• • •

Missing some Tweet in this thread? You can try to force a refresh
 

Keep Current with David Elfstrom

David Elfstrom Profile picture

Stay in touch and get notified when new unrolls are available from this author!

Read all threads

This Thread may be Removed Anytime!

PDF

Twitter may remove this content at anytime! Save it as PDF for later use!

Try unrolling a thread yourself!

how to unroll video
  1. Follow @ThreadReaderApp to mention us!

  2. From a Twitter thread mention us with a keyword "unroll"
@threadreaderapp unroll

Practice here first or read more on our help page!

More from @DavidElfstrom

10 Aug
Only at full speed does one of these units provide 2 ACH in a 750 sqft classroom with 10' ceiling height, at 65 dB(A) noise.
Min ventilation code 2.7 ACH for ages 5-8.
So for a non-mechanically ventilated classroom need another unit to achieve bare minimum. @caryn_lieberman
Keep in mind the target for the pandemic should be a lot more than bare minimum. Harvard TH Chan School of Public Health recommends 5-6 ACH.

On low the unit is quiet but provides less than 1 ACH

schools.forhealth.org/risk-reduction… Image
That particular classroom also had a unit ventilator, so it likely has adequate ventilation. ASHRAE has provided sample calculations including sizing supplemental filtration:
Read 8 tweets
28 Jul
JULY 26, 2021—Ontario Society of Professional Engineers @O_S_P_E calls upon @sflecce & @ONgov to immediately consult with subject matter experts and address #airborne transmission in schools before more outbreaks occur: ospe.on.ca/advocacy/engin… /1
"Engineers know if we are going to combat the Delta and future variants and a potential fourth wave, the need for proper ventilation and filtration of indoor air is paramount" says @O_S_P_E. /2
"Engineers know that air quality is bigger than COVID-19" says @O_S_P_E.

"The cost of investment is small compared to the benefits we will reap in finance, health and wellness" /3
Read 10 tweets
26 Jul
Ontario Professional Engineers working in building facilities management, especially but not limited to public buildings with known poor ventilation such as schools: ASHRAE unequivocally states #COVIDisAirborne. There is a Duty to Report involving safety. /1 ImageImage
When the reckoning comes regarding failure to prevent #airborne transmission of SARS-CoV-2, Professional Engineers should be on the right side of history. Continue to follow the Professional Practice Guideline.
@PEO_HQ @O_S_P_E /2
Engineers need to go on record with their employer when they have identified a safety concern. They may have limited options to affect change, but they do have a duty to report it up the chain of responsibility. Write that memo. Come away with a clear conscious. /3
Read 5 tweets
13 Jun
1/ Oh hai Clinical Excellence Commission @NSWCEC. Looks like you wrote an IPAC Manual for Quarantine Hotels recommending air pressure differential limits without considering the implications. Would you like some assistance with that? THREAD... Clippy from Microsoft Office 97Image of web page showing IPAC Manual for Quarantine Hotels
2/ Allow me to introduce you to Bernoulli's Equation as it pertains to flow through an orifice. In this case, under and around a door. Air flow through a sharp-edged circular orifice. Q = Cd * Af
3/ Bernoulli's equation allows us to predict airflow from a pressure difference, and vice-versa. The Florida Energy Center tested various orifices for flow & pressure difference. ba-pirc.org/casestud/retur… Using these results I calculate a Cd of 0.71 for various slots. Table from Florida Energy Center study on return air paths s
Read 21 tweets
25 May
1/ Dental office #COVIDCO2. The perfectly operable window is closed. 🤦‍♂️ THREAD... Handheld CO2 monitor (ARANET4) in front of a window, with th
2/ At the end of my visit, in a 144 sqft room with 9' ceilings, the hygienist and myself, it reached 1500 ppm. Overall rebreathed fraction of air from others reached 2.8%. The door to the operatory was open 1 inch. Chart of CO2 readings, showing initial value of 1325 ppm and
3/ I believe this is the outdoor air intake for the whole building. Located behind two air conditioner outdoor units. Rusty grille approximately 12 inches x 12 inches on the side
Read 10 tweets
21 May
1/ The Delta Fredericton has central corridor air pressurization and shared washroom exhaust. Lower floors may have inadequate pressure allowing air to flow out of suites. Failure of an exhaust fan can lead to direct connection between all suites on same shaft, @ShiftNB
2/ This style of ventilation & exhaust is disproportionally prevalent in Ontario apartment building outbreaks. Before concluding fomite transmission a more detailed analysis by subject matter experts (building science) is required. @DFisman @IPACCanada docs.google.com/spreadsheets/d…
3/ More detail about the possible mechanisms from building science in this thread:
Read 8 tweets

Did Thread Reader help you today?

Support us! We are indie developers!


This site is made by just two indie developers on a laptop doing marketing, support and development! Read more about the story.

Become a Premium Member ($3/month or $30/year) and get exclusive features!

Become Premium

Too expensive? Make a small donation by buying us coffee ($5) or help with server cost ($10)

Donate via Paypal Become our Patreon

Thank you for your support!

Follow Us on Twitter!

:(