Reading through @OtherProfGreen summary of the 9th August #UK event, the similarities to the 25th August 2018 #Australian separation event across the #NEM are very interesting to observe.
Firstly, they are all attributed to lightning strikes.

And although the #UK one was easy to identify, the #QLD one took a bit of forensic investigation as it happened at a time that no weather warnings were out for the area.
Both events attribute an initial loss of generation due to disconnection of #distributed #generation #DG

I will get back to this point later, because it is probably the most interesting aspect of both events!!
The combination of events that followed lead to decrease in the system #frequency at #RoCoF that is considered quite high (although as the #SAblackout event showed us in 2016, we should be prepared for much higher values)
The lack of "reserve" (and I am not using the term spinning here because we can, if we want, get reserve functions out of #wind and #solar - #FPPT) meant that the frequency dropped to UFLS - LFDD limits of 49Hz
This meant that a protection that was specifically designed to protect the system when frequency drops to 49Hz actually worked as it was supposed to - in both occasions.
Side note here but I like the two different terms for the same protection used in the #AU and #UK reports:

UFLS -> under-frequency load shedding
LFDD -> Low-frequency demand disconnection
Once UFLS - LFDD was activated and system frequency was able to recover - this was a bit more complex in the #NEM because the UF led to South Australia disconnecting as well - the system was able to progressively recover with, oddly enough ~1GW of load disconnected in each event
Now to the two bits I find juicy - more in a follow-up blog post:
1) Immediately after each event there was a substantial part of #DG that was disconnected. This has led to the ongoing discussion in AU about revision of the standard and inverter response to network events
You can find some examples on how different inverters may respond to network events here:

pvinverters.ee.unsw.edu.au

and our topical presentation at @cigreaus #cider19 yesterday!
2) Are frequency #markets affecting (IMHO killing) the system during these events? Mandate a level of support or reserve each unit needs to have available (including AGC #solar and #wind) and keep the system frequency tight within bands...

• • •

Missing some Tweet in this thread? You can try to force a refresh
 

Keep Current with Georgios Konstantinou

Georgios Konstantinou Profile picture

Stay in touch and get notified when new unrolls are available from this author!

Read all threads

This Thread may be Removed Anytime!

PDF

Twitter may remove this content at anytime! Save it as PDF for later use!

Try unrolling a thread yourself!

how to unroll video
  1. Follow @ThreadReaderApp to mention us!

  2. From a Twitter thread mention us with a keyword "unroll"
@threadreaderapp unroll

Practice here first or read more on our help page!

More from @GeoKonstantinou

Jan 13, 2023
Back in 2019, we finished an UG project creating a timeline of #HVDC projects 🌎🌍🌏 and also added the what was then the newly proposed 🇦🇺🇸🇬 #suncable project.

This just looked at one aspect (the most technically challenging of all ⁉️) the undersea cable.

1/x
I also wrote a (very short) article for the #VSC #HVDC newsletter that @OfficialUoM Prof. Mike Barnes was editing on the news coming out of Australia

Here are some figures that might help put the #suncable project in context.

2/x Image
*These are from 2020 when the project was the Australia - Singapore Power Link (ASPL) and part of Yihong Li's UG thesis @eetunsw

1. Cable Length vs Capacity. The 2 🟢at ~1400MW are the ~700km, 515kV & 525 kV 🇬🇧🇩🇰& 🇬🇧🇳🇴projects commonly used as comparison

3/x Image
Read 11 tweets
Aug 27, 2019
OK, most of the following is textbook stuff on #HVDC but just a quick reference for what a "low-voltage metallic return" - the faulty part of #Basslink - is used.
Basslink is a monopolar HVDC system and the original design was based on an earth return. This is quite typical of monopolar #HVDC systems as it reduces cost (requires only one cable) and losses (again because of one cable)

ptd.siemens.de/IEE_HVDC_0306.…
The reasons #Basslink was eventually designed with a metallic return were mostly environmental (see link above) to avoid

"- Corrosion of long metallic structures
- Electrolysis effects of sea electrodes
- Electric and magnetic field effects"
Read 7 tweets

Did Thread Reader help you today?

Support us! We are indie developers!


This site is made by just two indie developers on a laptop doing marketing, support and development! Read more about the story.

Become a Premium Member ($3/month or $30/year) and get exclusive features!

Become Premium

Don't want to be a Premium member but still want to support us?

Make a small donation by buying us coffee ($5) or help with server cost ($10)

Donate via Paypal

Or Donate anonymously using crypto!

Ethereum

0xfe58350B80634f60Fa6Dc149a72b4DFbc17D341E copy

Bitcoin

3ATGMxNzCUFzxpMCHL5sWSt4DVtS8UqXpi copy

Thank you for your support!

Follow Us!

:(